The smaller tube is the output. The input is often located near the sealed off process tube.
An AC compressor is defined as a "High Temp" compressor. This designation is based on the expected input pressure based on the temperature of the evaporator.
In an AC compressor the evaporator is held near freezing which is relatively warm. A dehumidifier is also a high temp compressor.
Low temp compressors have a higher displacement and expect lower input pressures associated with much colder evaporators such as ice makers and freezers where the temp is well below freezing. Most fridge compressors are low temp units as that is the temperature of the icebox.
As a high temp unit they are better suited as the final compressor in a multi stage pump for high volume and relatively high pressure. They are quite happy taking in 60 PSI and outputting 250 PSI.
At freezing R22 has a vapor pressure of about 25 PSI. At 45 degrees on the evaporator the pressure would be about 76 PSI. On a hot day the condenser may run 140 degrees and condense at about 340 PSI.
The compressor would work hard but handle an input of about 50 PSI with an output near 300 PSI just fine.
Use a freon chart to see the expected pressures your compressor is designed to work with.
http://www.longviewweb.com/pressure.php
R12 is obsolete. R134a is close to it.
As far as fittings, just google the part number. It's the big number starting with a 2 in the upper left corner of the compressor label.
Do I have to do everything?
http://www.panasonic.com/industrial/inc ... 26A-6A.pdf